ryan_618
Senior Member
- Location
- Salt Lake City, Utah
On an inspection today I requested the reults of a GFPE test required by 230.95(C). To my surprise, I was told that the testing lab removed the breaker, took it off site, and performed the test in their lab. This was because their test set wouldn't provide enough current for even the lowest setting of the breaker. I rejected this test, as I believe it must be tested while installed, per the "first installed on site" language of 230.95(C). Of course, the testing lab says I am an idiot, and that they have never been made to do that.
Any thoughts?
Any thoughts?