meternerd
Senior Member
- Location
- Athol, ID
- Occupation
- retired water & electric utility electrician, meter/relay tech
Some of the better Fluke meters will tolerate voltage on a circuit when reading ohms, but it's a garbage reading. Others automatically switch to a volts scale if you try ohms on a hot circuit. I was called to a service by a lineman who had a Fluke but was reading weird ohms on the top jaws of an energized meter socket. I politely explained that he's lucky it was a Fluke, because people have been injured or killed doing the very same thing with a cheaper analog meter. A line side fault on a socket takes a LONG time to blow a primary fuse. Bottom line....you cannot read ohms on a live circuit. If the breaker is off, it isn't live. You can only read a transformer winding if the breaker is on but power is off. Question doesn't make sense to me. I'm betting the meter switched to volts and he thought it was still ohms. Look at the display and I'll bet it said V.