Oil filled pad mounted transformer

Merry Christmas
Status
Not open for further replies.

Sparky2791

Senior Member
Location
Northeast, PA
Occupation
Electrical Design
Does an outdoor oil filled pad mounted transformer require a ground wire be brought in with the feeders. I am thinking a supply side bonding jumper is required but the code takes you through steps that seem be exceptions make it not required. For example 250.30 A (2) Exception but I do not understand the requirements of 250.30 (A) (1)

Thanks for replying
 
I think an oil filled outdoor transformer would meet 250.30(A)(1) Ex.2 [I am on 2020 NEC] no?
 
I think an oil filled outdoor transformer would meet 250.30(A)(1) Ex.2 [I am on 2020 NEC] no?
That is what I am seeking guidance on but I believe you are correct. The ground is established at the service entrance so no need to pull a ground wire in with the service conductors? Can anyone clear up that exception? By the way I am under 2014 NEC.
 
The ground is established at the service entrance
Are we talking about a service or feeder?
I was picturing a campus type setup where you have something like 480V feeders to the oilfilled then 280/120 to said building.
Where is the service point?
Here is a info graphic from the 2014 handbook:
outdoor_transformer_grounding.png
 
For the most part, the actual transformer voltages are not important, a 12470V delta primary to a 480Y/277V wye secondary would require basically the same connections as a 480V delta to 208Y/120V transformer.

The fact the this transformer feeds a building versus a lighting panel is not important. The secondary is not an NEC service.
 