I've never dealt with fuel dispensers, but we work in natural gas compressor stations. Using EYDs on vertical installations outside of a building is strictly enforced by plant operations so they can drain..... just what I'm used to seeing in that industry.
501.15(B)(2) allows the boundary seal to be installed on either side of the boundary, but not required on both sides. However, it looks like the sealing requirements are more strict in 514.9, but I wouldn't have known better if I didn't own the handbook and read the comments. I can't even seem to figure out how they came to that conclusion.
501.15(B)(2) allows the boundary seal to be installed on either side of the boundary, but not required on both sides. However, it looks like the sealing requirements are more strict in 514.9, but I wouldn't have known better if I didn't own the handbook and read the comments. I can't even seem to figure out how they came to that conclusion.