" VI. Service Equipment - Disconnecting Means
230.70 General. Means shall be provided to disconnect all conductors in a building or other structure from the serviceentrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (2), and (3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."
For Guidance:
Chapter 8, A definition for POE
"Point of Entrance.
Within a building, the point at which the wire or cable emerges from an external wall, from a
concrete floor slab, or from a rigid metal conduit or an intermediate metal conduit grounded to an electrode in accordance
with 800.40(B)."
Okay, my point
Service entrance conductors entering a building.
We have seen that there are many different ideas as to how far a set of service entrance conductors can travel into a building before a disconnect is required. 5', 10', 15' in some jurisdictions.
If I can come into the building any of those distances, why not further? Why not 25', why not 50'?
What is the difference between 5' or say 15', which we know some jurisdictions permit, why not more.
Once the conductors are in the building I do not see what the difference is (I don't think current will know the difference either). 1' just into the building will cause the same problem just as the 1' portion that is 7' or more inside the building.
"...inside nearest the point of entrance..."
What does that really mean?
What is the real reason that this disconnect is being installed?
[ October 14, 2005, 08:04 AM: Message edited by: pierre ]
" VI. Service Equipment - Disconnecting Means
230.70 General. Means shall be provided to disconnect all conductors in a building or other structure from the serviceentrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (2), and (3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."
For Guidance:
Chapter 8, A definition for POE
"Point of Entrance.
Within a building, the point at which the wire or cable emerges from an external wall, from a
concrete floor slab, or from a rigid metal conduit or an intermediate metal conduit grounded to an electrode in accordance
with 800.40(B)."
Okay, my point
Service entrance conductors entering a building.
We have seen that there are many different ideas as to how far a set of service entrance conductors can travel into a building before a disconnect is required. 5', 10', 15' in some jurisdictions.
If I can come into the building any of those distances, why not further? Why not 25', why not 50'?
What is the difference between 5' or say 15', which we know some jurisdictions permit, why not more.
Once the conductors are in the building I do not see what the difference is (I don't think current will know the difference either). 1' just into the building will cause the same problem just as the 1' portion that is 7' or more inside the building.
"...inside nearest the point of entrance..."
What does that really mean?
What is the real reason that this disconnect is being installed?