Contractors & handyman both get this wrong for lack of skills or experience.Those are the only two options. GFCI is the simplest but often the old boxes are pretty small/
I almost always recommend a new circuit.
What options do you guys provide other than rewiring with NM or adding GFCI protection to solve the EGC issue?
I'll second 250.130(C) also note it has no amperage limitation, so you can use it for a range or dryer.250.130(C) is another option that complies with fire code.
Having a 3 wire receptacle on an ungrounded circuit is not a violation in and of itself.
I don't know the code by heart and don't have the book on me right now, but I'm 97% sure that's wrong.
Oh, yes, I forgot about putting it on a GFI. No problem, if you do that. I did it in 1999 as an apprentice, and not since then, so that's why I forgot.Generally speaking, a 3 prong receptacle can be installed on a 2 wire circuit as long as GFCI protection is provided and it is labeled properly.
You can add GFCI protection, you can pick up a ground, or you can pull a new circuit. Or all new service if they really want to do it right.
Thise are pretty much the only options.
Having a 3 wire receptacle on an ungrounded circuit is not a violation in and of itself.
And, any EGCs should not be connected to devices or to each other.Generally speaking, a 3 prong receptacle can be installed on a 2 wire circuit as long as GFCI protection is provided and it is labeled properly.
If the ungrounded receptacle serves one of the items in 250.114, like a refrigerator you might have an issue.Having a 3 wire receptacle on an ungrounded circuit is not a violation in and of itself.
Been told that those plug in GFCI testers are not valid for inspection purpose for that very reason. Only acceptable test is the test button on the receptacle or breaker.We replaced some 2 prong with gfci’s once. Then the inspector came along with his plug tester and it doesn’t trip. Threw us for a loop for a bit but found out the hand tester has to have a ground to test.
(3) In residential occupancies:
a. Refrigerators, freezers, and air conditioners
b. Clothes-washing, clothes-drying, dish-washing
machines; ranges; kitchen waste disposers; information
technology equipment; sump pumps and electrical
aquarium equipment
c. Hand-held motor-operated tools, stationary and fixed
motor-operated tools, and light industrial motor-
operated tools
d. Motor-operated appliances of the following types:
hedge clippers, lawn mowers, snow blowers, and wet
scrubbers
e. Portable handlamps
Well you could also replace it with a new "two prong".Those are the only two options. GFCI is the simplest but often the old boxes are pretty small/