Old 2 wire

Status
Not open for further replies.

Jnewell

Member
Location
Las vegss
I keep running into 2 wire setups with handyman who put 3 prong outlets and having to explain why that isn’t safe to customers. What options do you guys provide other than rewiring with NM or adding GFCI protection to solve the EGC issue?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Often, in older homes, a grounding receptacle is desired for a new point load, such as a computer setup, an audio/video system, a window A/C, etc. In such cases, I almost always recommend a new circuit.

This provides the double advantage of giving the new load a new, direct, well-grounded circuit, as well as relieving the existing wiring of the burden of supplying the new load.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Those are the only two options. GFCI is the simplest but often the old boxes are pretty small/
Contractors & handyman both get this wrong for lack of skills or experience.

In most States where 406.4(D)4 was adopted over 10yrs ago, the municipal-combination inspectors are walking right thru remodels without checking for it.

Apparently nobody needs to comply with this, or inspect for it, and the property will be subject to hidden, latent, or construction-defect law.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I almost always recommend a new circuit.

This method also triggers 210.12, but compliance is simpler with dedicated circuits, if contractors are willing to do it.

What options do you guys provide other than rewiring with NM or adding GFCI protection to solve the EGC issue?

250.130(C) is another option that complies with fire code.

However, this option also triggers 406.4(D)3&4&5 without the existing 2-prong plug that was originally permitted & inspected with the building.

Another option 406.4(D)2(a) has always been available for those who refuse, or can't handle the other requirements.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
250.130(C) is another option that complies with fire code.
I'll second 250.130(C) also note it has no amperage limitation, so you can use it for a range or dryer.
It however can be a stunt to fish that green wire into a old metal box.
Then you have the issue of really old boxes with no ground screw hole.
I prefer to make my own over using the grounding clips:
1641402054265.png
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
You can add GFCI protection, you can pick up a ground, or you can pull a new circuit. Or all new service if they really want to do it right.

Thise are pretty much the only options.

Having a 3 wire receptacle on an ungrounded circuit is not a violation in and of itself.
 

Mr. Serious

Senior Member
Location
Oklahoma, USA
Occupation
Electrical Contractor
Generally speaking, a 3 prong receptacle can be installed on a 2 wire circuit as long as GFCI protection is provided and it is labeled properly.
Oh, yes, I forgot about putting it on a GFI. No problem, if you do that. I did it in 1999 as an apprentice, and not since then, so that's why I forgot.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
You can add GFCI protection, you can pick up a ground, or you can pull a new circuit. Or all new service if they really want to do it right.

Thise are pretty much the only options.

Having a 3 wire receptacle on an ungrounded circuit is not a violation in and of itself.
😳

Layed out right here how to do it. 406.4(d)
 

NTesla76

Senior Member
Location
IA
Occupation
Electrics
If there were a two wire system and someone at some point in time came along and installed 3 prong receptacles on said two wire system, that would be non compliant. I agree add gfci protection, an egc, or I don't see why you can't install a 2 prong receptacle since the 3 prong receptacle was wrong anyway.
 

LT Sparky

Member
Location
Farwell, TX, United States
Occupation
Estimator Project Manager
We replaced some 2 prong with gfci’s once. Then the inspector came along with his plug tester and it doesn’t trip. Threw us for a loop for a bit but found out the hand tester has to have a ground to test.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
We replaced some 2 prong with gfci’s once. Then the inspector came along with his plug tester and it doesn’t trip. Threw us for a loop for a bit but found out the hand tester has to have a ground to test.
Been told that those plug in GFCI testers are not valid for inspection purpose for that very reason. Only acceptable test is the test button on the receptacle or breaker.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Had to tell an Inspectigator that.

The plug in testers leak a small amount of current to the ground. If there’s no ground, then it doesn’t leak.

So unless he wants to ground himself and grab the hot, he better go to the GFCI, push the button, and make sure all downstream receptacles are dead. 👍
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
If its an occupied dwelling a scrupulous inspector could really dig into 250.114(3), for example information technology equipment.

(3) In residential occupancies:
a. Refrigerators, freezers, and air conditioners
b. Clothes-washing, clothes-drying, dish-washing
machines; ranges; kitchen waste disposers; information
technology equipment; sump pumps and electrical
aquarium equipment
c. Hand-held motor-operated tools, stationary and fixed
motor-operated tools, and light industrial motor-
operated tools
d. Motor-operated appliances of the following types:
hedge clippers, lawn mowers, snow blowers, and wet
scrubbers
e. Portable handlamps
 
Last edited: