Is there an NEC requirement or recommendation that taped connections in a gutter box should be tested or inspected at some interval?
I was recently on a team that investigated the events that led to an electrical fire that burned down the historic El Portal Market at the entrance to Yosemite National Park. The fire originated in the ?gutter? box between the overhead service connection and three individual revenue meters. The conductors connecting the meters were spliced to the service conductors using kerneys in a tandem arrangement. One phase became grounded to the cover of the gutter box burning a hole in the cover igniting combustible materials that set the building on fire. The electrical service was reliable for at least forty years and there was no record that the connections in the gutter box had ever been checked.
I was recently on a team that investigated the events that led to an electrical fire that burned down the historic El Portal Market at the entrance to Yosemite National Park. The fire originated in the ?gutter? box between the overhead service connection and three individual revenue meters. The conductors connecting the meters were spliced to the service conductors using kerneys in a tandem arrangement. One phase became grounded to the cover of the gutter box burning a hole in the cover igniting combustible materials that set the building on fire. The electrical service was reliable for at least forty years and there was no record that the connections in the gutter box had ever been checked.