• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Old homes with no ground

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Note if you are changing out the receptacles, 406.4 requires to new ones to be AFCI or AFCI protected so I would try a dual function breaker first.
With knob and tube the breaker may be problematic but try it to see so you don't have to address AFCI receptacles,
 
Several times have left 2-prongs and ran new circuits to provide a 3-prong ea room
Yeah depends on what one is looking to accomplish. I would be more concerned about replacing the old wiring which may be at the end of it's useful life and have questionable insulation and connections. I'm not too worried specifically about "not having a ground"
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I was always told that the number of "labels" with the device is the max

Good to know

Thank You


Sent from my iPhone using Tapatalk
Mod Note: Please update your profile to show occupation/ relationship to the electrical industry
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
Many older houses have shallow boxes, some bevel back. You would have a hard time with most and it would be impossible to put a GFCI into a bevel back box.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Remember, GFCIs will work without an EG but you become that path to earth if there is a fault. It will hurt.
Generally there is a limit to the length of conductor on the load side of a GFCI, not the # of devices.
Limit on length of wire?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Yes. Some leakage occurs.
I assume it is length limit from the GFCI breaker and not the receptacle GFCI, correct?

What is the length limit?

ETA, you know, I vaguely remember I read something on this year's ago. I will check in the UL book and see if it was there.
 
Status
Not open for further replies.
Top