I recognize this is a message board for professionals, but I need some advice after having some questionable electrical work performed.
I have a 70 year old house with an underutilized 100 amp service. Several years ago I had an electrician upgrade and rewire the old cloth wrapped wire from the meter to the main panel. Now I am in the process of installing a subpanel-this is what I unraveled during the installation.
The meter is currently not grounded via a copper grounding rod or water pipe. It does appear to be grounded to the power pole via the solid strand cable anchored to the house which the main feed comes in on.
In the meter, the electrician connected the hot wire to one of the hot lugs, a ground wire to the neutral lug, and a neutral wire to the other hot lug. An unused red wire had been installed to supply 220v at a later time (I am guessing). These all run through PVC conduit to my main panel, which is not grounded with a copper grounding rod or water pipe connection.
In the main panel, the hot wire goes to the breakers, the ground and the "neutral" (which is actually hot) goes to the neutral bar. The red wire is capped off and loose in the box. The hot wire has a jumper that connects both breaker lugs.
While this has been supplying my house for several years now without burning down or electrocuting anyone, it seems to go against everything I know about modern residential wiring. I believe at the meter, the ground should be removed from the neutral lug, the neutral should go back to the neutral lug, and the red wire be connected to the other hot lug. At the panel, the hot jumper should be removed, the red wire should go to the (now unused) other breaker lug and the neutral should go to the neutral bar which is bonded to the panel with a new copper ground rod and water pipe ground. Does this make sense? I want to get a game plan for when the next electrician comes out to fix this mess if it indeed needs fixing-and before the installation of my sub panel.
Thanks in advance-the board has been a great help.
Adam
I have a 70 year old house with an underutilized 100 amp service. Several years ago I had an electrician upgrade and rewire the old cloth wrapped wire from the meter to the main panel. Now I am in the process of installing a subpanel-this is what I unraveled during the installation.
The meter is currently not grounded via a copper grounding rod or water pipe. It does appear to be grounded to the power pole via the solid strand cable anchored to the house which the main feed comes in on.
In the meter, the electrician connected the hot wire to one of the hot lugs, a ground wire to the neutral lug, and a neutral wire to the other hot lug. An unused red wire had been installed to supply 220v at a later time (I am guessing). These all run through PVC conduit to my main panel, which is not grounded with a copper grounding rod or water pipe connection.
In the main panel, the hot wire goes to the breakers, the ground and the "neutral" (which is actually hot) goes to the neutral bar. The red wire is capped off and loose in the box. The hot wire has a jumper that connects both breaker lugs.
While this has been supplying my house for several years now without burning down or electrocuting anyone, it seems to go against everything I know about modern residential wiring. I believe at the meter, the ground should be removed from the neutral lug, the neutral should go back to the neutral lug, and the red wire be connected to the other hot lug. At the panel, the hot jumper should be removed, the red wire should go to the (now unused) other breaker lug and the neutral should go to the neutral bar which is bonded to the panel with a new copper ground rod and water pipe ground. Does this make sense? I want to get a game plan for when the next electrician comes out to fix this mess if it indeed needs fixing-and before the installation of my sub panel.
Thanks in advance-the board has been a great help.