drcampbell
- The Motor City, Michigan USA
- Registered Professional Engineer
Situation: Old house with 2-wire NM cable concealed in the walls, not feasible to replace the cable or add a ground wire.
406.4(D)(2)(c) seems to permit the use of 3-conductor grounding-type receptacles if they're ground-fault protected and labeled.
But 250.114 seems to require certain appliances to be grounded, apparently without exceptions.
Two questions come to mind:
Does anybody know of a source of cover plates permanently engraved with the required messages "GFCI Protected" and "No Equipment Ground"? Sharpies look unprofessional and Post-It notes lack permanence.
Does 250.114 supersede 406.4(D)(2)(c), and if so, in the case of a non-double-insulated window air conditioner (among other appliances) with a 3-wire cord and a 3-conductor plug,
how is the average homeowner/tenant supposed to know that the normally non-current-carrying metals parts shall be connected to an equipment-grounding conductor, and they're not supposed to plug it into a 3-conductor receptacle so labeled?