Old Manufactured home panel.

Status
Not open for further replies.

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
I have to run about 250 feet cause this crappy Manufactured park had this feeder go straight through two other property and a phase was lost and I am not going to fix the wire anyway since its only 2/0 aluminum on a 200 amp breaker.
Either way. What do you think the most complaint way to set a new meter with main breaker. meeting Power company tomorrow.
Was thinking of seeing of there cool if I run a stub up to the center cavity were there feeders are coming in.
I don't want to reuse this box cause its only 16" from grade and rusted through the bottom. It's really up to power company how they want me to address this.
This park is really sketchy some of the Mains are just direct buried wire only 12" deep. I hit a water main once that was 6" lol.
 

Attachments

  • 0CEC41AB-FD26-4118-8425-49660434DAD2.jpeg
    0CEC41AB-FD26-4118-8425-49660434DAD2.jpeg
    87.2 KB · Views: 22
H frame and all the meters need changed. Maybe do a utility tap box with meters nippled to or unipack if they're all tapped of that center box and parts available.

That park won't like the bill or estimate for sure.
 
Utility are coming in the center. Customers come below each of the small panels.
Utility won’t help even through there crap is not correct if I want a pad mount Tran to come into or a underground splice box I have to dig from there existing pad mount about 500 feet of drive.
It’s annoying cause they admit it’s there line under the road but won’t fix it
 