Old Post HR's

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Came across this old thread. So if you had EMT with circuit out of a panel to a box right outside the closet then switched over to MC cables out to a hr box in the field would you consider the MC cable "homeruns"? Thanks.

 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you had one circuit in both EMT and then MC cable IMO the entire run would be a homerun.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
The circuit home runs. Makes no difference what it does it with, as long as it goes from the panel to the load without supplying anything else along the way.

-Hal
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
I think you should rfi what they mean by home run.
Since this is likely a spec section and the OP is likely asking in regards to estimating and installation, I don't recommend asking. I can find many specs that have stringent requirements for MC, like inside walls with xx feet to a junction box. When it is written this way, I would choose to make my own interpretation, and dispute the Engineer if he didn't like it. What I generally make my guys do in this situation is, a conduit homerun to the area and MC to the receptacles. 25 feet or so is OK. Lighting is the tricky one.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
My opinion is that changing wiring methods does not change what is the home-run portion of a circuit.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Since this is likely a spec section and the OP is likely asking in regards to estimating and installation, I don't recommend asking. I can find many specs that have stringent requirements for MC, like inside walls with xx feet to a junction box. When it is written this way, I would choose to make my own interpretation, and dispute the Engineer if he didn't like it. What I generally make my guys do in this situation is, a conduit homerun to the area and MC to the receptacles. 25 feet or so is OK. Lighting is the tricky one.
Why fight later when you can avoid it? You are not the guy that gets to interpret what the spec means if it is not clear to you.
 