..is there a good reason to replace the panel with a new circuit breaker panelboard?..
In commercial building zones, with equipment listed over 10K AIC, selecting fast fuses can reduce AIC & equipment damage. By comparison, in laboratory Short-Circuit tests, the fastest breakers result in equipment blown off walls and massive fire-balls engulfing the room.
In residential zones under 10k AIC fuse boxes that don't except modern AFCI's are usually replaced, but without knowing if those AFCI's will hold.
- but are you saying that using AFCI breakers on an existing receptacle circuit may be iffy? (I have seen a couple issues of this situation.)
+1 or 2 if you count the first reply.You have listed NO GOOD REASON to replace this panel board.
Is there a good reason to replace that you have not told us?
I think, in this case, the options are 1. don't replace, or 2. replace with circuit breaker panelboard.