hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
The thing just seems like a terrible idea to me.
It doesn't have snap action.
The contacts don't wipe.
There's no arc chute.
I'll bet most electricians or firemen would never dream such a thing existed.
There's no labeling to warn of what it does. (or more importantly, what it doesn't do )
The only purpose it could possibly serve seems to me to be way too trivial to warrant it's use.
Since the contacts "make" before the meter stabs "break" no snap action, contact wipe, or arc chute is required. On the newer ones their is a warning label. Meter removal is supposed to be done by authorized personnel only. (With most POCOS electricians removing meters are not authorized personnel and can lead to jail time and fines, though rarely enforced)