"old wives' tale" code
electrofelon
Cherry Valley NY, Seattle, WA
We usually talk about code compliance - that is doing something in a way that satisfies a code requirement. Lately though I have been hearing a lot or false code, that is people talking about and/or doing things that arent code but are said to be. These things are usually 'overkill' and thus not a safety issue, but they do waste time, materials, and money. Here are some of the ones I have heard recently, from practicing electricians:
1. Luminaires within 6 feet of a tub or shower need GFI protection.
2. The NEC requires lights to be on a 15 amp circuit.
3. Hydromassage tubs need an insulated ground, so you have to use a 12-3 and re-identify the red as the ground (partially true, but this guy missed the exception).
4. Then of course there is the number of cables per staple and romex connector......
I am by no means immune to this, for years I thought you couldnt run phone/coax and NM through the same bored hole
Perhaps its a good idea to occasionally look for code references for things that we hold as gospel.
Re: "old wives' tale" code
Back in 1992 on box of romex connectors we used, it stated 2 14/2 or 1 12/2 per connector.
The boxes I see today say 2 14/2 or 12/2 per connector
Here's a few I was thinking of:
1- Cannot put spices in a panelboard.
2- Cannot use panelboard as a raceway.
3- Cannot use 4 wire cable in a dwelling (Bk,Red,Blue,Wht).
4- Cannot use Brown, Orange, Yellow, Grey conductors in a dwelling.
5- Cannot enter a type NM cable into a florescent fixture.
1 must use black red blue on 3 phase 120/208
2 must have a outside recpt by each outside door
3 emt staped 6" from box
4 all halls need 1 recpt and every 10' :roll: almost true
5 12' spaceing applys to every room
Each bathroom must have a GFCI receptacle not just protected by Ground fault (Got nailed for this about 6 mos. ago)
1 - Switches are required IN every room/area that requires a switched outlet
2 - 3-ways are actually required
I am sure some of you ppl can remember some of the other "code violations" I have debated - at great length :) - these two are right at the front of the cranium.
Along these lines, I am curious to know if anyone was tagged for installing receptacles upside down (i.e., ground was up and it is required to be down, or vice versa)?
We always install ours ground up as a company standard. Got dinged by a project engineer once who referred me back to the drawings. There was an elevation view that showed a typical wall section with cabinets, sink, applicances and wiring devices. The receptacles were drawn ground down. He said "see?". We didn't argue, we just changed them. Sometimes you pick your battles.
1. Grounding does something
2. You need two forms of grounding
3. Lightning doesn't damage buildings with grounded services
4. Some electrodes are better than others
5. Grounding gets rid of static charge
6. Good grounding clears faults.
7. Pool heaters need ground rods
8. Grounding reduces the risk of fire or shock
9. UL? Whats a UL? Listing? Where can I get a copy of the list?
10. 3-ways are required when there are two entries into a room or area
11. Any circuit breaker that fits must be okay to use.
12. The NEC is the only code or reference that effects the electrician
13. The Florida Building Code makes sense.
14. Inspectors have an easy job
15. Gorunding does something.
Charlie, Yes. Indiana Heart Hospital. The Inspector called out Receptacles had to be Installed ground up (1500 receptacles) I asked Him. Where is that in "Your" book ? Never did hear from Him again. (Is it OK in the Forum to mention that job by name)?
Bryan, Don't all Building Codes make cents? :D
Nevermind; I'm mistaken again, you said sense. Because the Building Codes frequently cost somebody some cents. :D :D
While these are urban legends Celtic ,3 ways are required when there are more than 6 steps or there is a landing in the stairwell with access to another area in that case a 4 way would usually be what would be installed.
Infinity #3 there was a time not sure if still there but NYC did prohibit 4 wire BX to be installed.
Bphgravity your #13 gave me a good laugh since Floridas codes are governed by what are the rules today. ;)
Some others that are out there..............
1-anti oxide compound is required on all AL connections
2-2 in.NM connectors require a plastic bushing
3-Nm is suitable in pvc conduit under a slab
4-The wiring for an outdoor a/c unit must match the max breaker rating
5-Exterior receptacles above 8 ft do not require GFCI protection
6- Nm exposed in a garage that is below 8 ft requires conduit for protection
7-Service disconnects that fall above but behind an a/c condensor must be relocated
Where does it say that 3-ways are required?
"Usually" does not mean required.
We can hash this out over at Are 3-way switches code or just convenience? , again :p
In summary. What introduced all of these anyway. Misinterpretation, lack of communication, lack of education....g-d I love this Forum! No where else could One receive such an education as this... :)
I think the all time #1 answer is:
GFCI is required within 6' of a sink.
Steve