Older wire at weatherhead
floatr
tn
I noticed something different about my weatherhead an wanted more information on its purpose an where it is to terminate.
Atop the weatherhead before my neutral enters it i have a #4 copper wire crimped to it.
It then runs down pipe to meter area.
Were these use a long time ago as a ground?
Is that part of wire considered to be "their side" ?
Thank you
Thank you
Local EMC's around here used to require bare copper from weatherhead thru meter to ground rod, tough to get it in sometimes because we weren't allowed to cut it
Also #4 for 200 amp service, even if going to ground rod
They stopped requiring running to weatherhead
Thank you
Based on your other thread and the comment about the power company telling you to hook it back up, what you have is a local power company requirement, in my opinion. The NEC is, and has been, silent about a hookup like this.
Thank you Dave ,for the reply.
I will ask the inspector im meeting with in the morning about removal of it .
I know they go by latest codes though .
Its terminated in meter box now.Before it was not attatched to anything on that end.
I wasnt sure if it had went to grounding rod or meter box .
Hopefully i can have it disconnected on their end before the weatherhead. An eliminate it totally.
New ground rod installed with #4 to neutral bar.
I wasnt sure if it had went go to grounding rod or meter box .
The GEC wouldn't go from the weatherhead to the meter and no further. That would accomplish nothing. It should be run (in some areas) from the weatherhead down to a ground rod or other electrode.
We have one POCO that still requires on overhead services that the GEC be tied to the neutral (grounded conductor) at the weatherhead and not in the meter base.
Then we have another that requires it in the meter and not the weatherhead. Either way is acceptable to the NEC.
I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.
If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.
A reminder to all members, if you see a questionable post, feel free to report it by clicking the
button at the bottom left corner of the post.