chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- 60 yr old tool twisting electrician
If I need to bury a 24V control cir. from Gen Set to ATS. I would bury it 18 to top of RNC. As per Dons previous posts 725.3 states only a handful of sections from 300 apply to class 2 cirs. 300.5 isn't one of them. 300.5 column 3 states " Nonmetallic Raceways Listed for Direct Burial Without Concrete Encasement or Other Approved Raceways". This doesn't say what is in the RNC. Therefore, even if the RNC only has a pull string, shouldn't it still be 18 to the top? How deep would you bury it in the crap soil (rocks) you dig in?