One 8 AWG wire can handle about 50 Amps. Two would handle 100 Amps.

Merry Christmas
Status
Not open for further replies.
I'll have to think it through, it was many years ago. I was working on the roof where the ac unit was not working . As I remember the feeders came through the roof into a j box where 1 phase- 2 conductors. Were sliced by split bolt with 2 more conductors and one conductor went to ac and one to heat unit. The same was done with the other phase. I could be wrong but I remember hearing the heat and the ac aren't on at the same time so it can work.

The #8's were spliced by a split bolt & then served the AC portion & the heat portion separately. I say this is not a parallel conductor situation. Just one branch circuit going to separate but related loads in your equipment.

...................................................................................................................................................................................................................................................................................................................


The oven landed in a 4-11 behind the oven 2 blacks,2 red's. Connected to the oven whip.

..................................................................................................................................................................................................................................................................................................................

The oven was non compliant, you can't parallel conductors smaller than #1/0
 
Last edited: