Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Hello!
I am working on a project for a client which is a large commercial building with 2 separate tenant spaces. There is a 3-hour firewall between the 2 spaces. Each space has its own electric service, separate POCO pad mounted transformers feeding each space, and an electric room with service equipment. One service is 2500A the other is 1000A, both are 277/480V 3-phase.
The tenant in each space is the same company and the service in space #1 has lots of spare load based on electric bills peak demand history, they want to take 1000A feeder from Tenant Space #1 and feed equipment in Tenant space #2. Ignoring the fact that there will be an electric feed metered from space #1 in space #2 because the buildings landlord is OK with it, this seems like it is in violation of NEC, but I cannot nail down what section to cite or if anything would allow this as an exception, like a sign at each service or something. I was going to research this tonight but thought I would start here first to get some code back up before a meeting we have regarding this.
Thanks for the replies!
I am working on a project for a client which is a large commercial building with 2 separate tenant spaces. There is a 3-hour firewall between the 2 spaces. Each space has its own electric service, separate POCO pad mounted transformers feeding each space, and an electric room with service equipment. One service is 2500A the other is 1000A, both are 277/480V 3-phase.
The tenant in each space is the same company and the service in space #1 has lots of spare load based on electric bills peak demand history, they want to take 1000A feeder from Tenant Space #1 and feed equipment in Tenant space #2. Ignoring the fact that there will be an electric feed metered from space #1 in space #2 because the buildings landlord is OK with it, this seems like it is in violation of NEC, but I cannot nail down what section to cite or if anything would allow this as an exception, like a sign at each service or something. I was going to research this tonight but thought I would start here first to get some code back up before a meeting we have regarding this.
Thanks for the replies!