One conductor in multiple lugs

Merry Christmas
Status
Not open for further replies.
Paul B said:
OK so are you folks saying it is OK to put (1) grounded conductor and (1 or more EGC's) under one terminal? I do this all the time and never been cited for it.
408.41 "Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor"
 
georgestolz said:
Can somebody explain how they would apply 110.3(B) to the original question? I see dots, but I'm not connecting them too well.


If the Terminals are not rated for the conductor size, then no good right?

Could a Conductor be "split" to create a size listed in the manufacturers instruction? I don't think it would be OK but maybe.


110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

Tom
 
If the terminal is rated for between 14 and 4 copper, and a conductor is installed that is between those two sizes, has the terminal's listing been compromised?

I was thinking, is it a violation of the listing of the conductor, perhaps? :-?
 