I got hurt yesterday in a a one in a million event. I got a call to stop on my way home and check sparks in an AHU. When I got there I pulled out the disco pullout and got a ladder to inspect the units.
As I climbed up I grabbed the allthread supporting the units then grabbed the copper lines and got hit so hard I could't let go. Seemed like 5 seconds before the ladder and myself hit the floor.
Tester showed 210V between the copper and the allthread. High leg fault right?
There where a number of disco's at the service. The building is 40 years old and high leg is on C. Turned off one at a time untill fault clears. Disco in question was 3? but used as single phase, A and C hooked up.
Pulled out C and capped it off.
Put AHU pullout back in disco and show no volts allthread to copper. I put one prong of tester in a near by rec neutral slot and find allthread clear but 120V to copper.
I opened unit to find all kinds of wire lying in the bottom not capped off. Some genious disabled the heat strips by pulling one conductor off each and left them touching the unit. Cut and capped those.
Heres something puzzling. In the AHU's if you test from each lug to the EGC you get 120V. Why didn't the fault/faults clear? I also tested each lug to allthread and nothing. Tested continuity between allthread and EGC and had nothing.
I'm sorry I didn't think about pics untill I got home.(I was a little shaken up) I need to go back tomorrow so I'll get some.
As I climbed up I grabbed the allthread supporting the units then grabbed the copper lines and got hit so hard I could't let go. Seemed like 5 seconds before the ladder and myself hit the floor.
Tester showed 210V between the copper and the allthread. High leg fault right?
There where a number of disco's at the service. The building is 40 years old and high leg is on C. Turned off one at a time untill fault clears. Disco in question was 3? but used as single phase, A and C hooked up.
Pulled out C and capped it off.
Put AHU pullout back in disco and show no volts allthread to copper. I put one prong of tester in a near by rec neutral slot and find allthread clear but 120V to copper.
I opened unit to find all kinds of wire lying in the bottom not capped off. Some genious disabled the heat strips by pulling one conductor off each and left them touching the unit. Cut and capped those.
Heres something puzzling. In the AHU's if you test from each lug to the EGC you get 120V. Why didn't the fault/faults clear? I also tested each lug to allthread and nothing. Tested continuity between allthread and EGC and had nothing.
I'm sorry I didn't think about pics untill I got home.(I was a little shaken up) I need to go back tomorrow so I'll get some.