I have a situation where I've driven two ground rods into the garden on the other side of the basement wall where the water main comes into the basement .
It's not a cement wall, the foundation actually stops a few feet above the basement floor, and maybe six inches above grade outside the wall.
Can I just run a single GEC from the meter/main through the basement to the water grounds (one clamp on each side of the meter) then continue on through the wall to hit each of the ground rods?
Keep in mind that here in MA we usually run the ground rod GEC to the meter socket and the water ground to the panel with the main breaker. But in this case the main breaker is in the meter socket, so both would run to that.
My concern is that each of the electrode systems need their own GEC to bond to the service grounded conductor.
It's not a cement wall, the foundation actually stops a few feet above the basement floor, and maybe six inches above grade outside the wall.
Can I just run a single GEC from the meter/main through the basement to the water grounds (one clamp on each side of the meter) then continue on through the wall to hit each of the ground rods?
Keep in mind that here in MA we usually run the ground rod GEC to the meter socket and the water ground to the panel with the main breaker. But in this case the main breaker is in the meter socket, so both would run to that.
My concern is that each of the electrode systems need their own GEC to bond to the service grounded conductor.