Don I do not think we are talking about the same installation.Originally posted by don_resqcapt19:
Bob,
Even if they are service rated transfer switches the grounded conductor from the transfer switch to the generator and then to the other transfer switch would create the violation.Don I had assumed a service entrance transfer switch which in that case I did not see a violation.
Don
So am I. While the transfer switch may be the service disconnect, the conductors that leave the transfer switch and go to the generator are, in my opinion, on the load side of the transfer switch and therefore a violation.I am picturing a service rated transfer switch that is the buildings service disconect. In that case these multiple paths are on the supply side of the service disconnect and the NEC does not prohibit multiple grounding on that side.
Don I can not agree to that, the conductors do not leave the transfer switch and go to the generator.Originally posted by don_resqcapt19:
Don
While they do supply the transfer switch, they are still on the load side of the service disconnect.The conductors leave the generator and supply the transfer switch.
I can not see how that is possible.Originally posted by don_resqcapt19:
Bob,
Don