S speedypetey Senior Member Location Hudson Valley, NY Feb 14, 2006 #1 ...on a neutral bar. I know it's code but where is it. For the life of me I can't find it.
B benaround Senior Member Location Arizona Feb 14, 2006 #2 Re: One grounded conductor per hole..... It's in the information that comes with the equipment.
F fc Senior Member Location New Jersey Feb 14, 2006 #3 Re: One grounded conductor per hole..... 110.14 (A)
S speedypetey Senior Member Location Hudson Valley, NY Feb 14, 2006 #4 Re: One grounded conductor per hole..... 110.14 (A) That's it. I haven't needed to read it in so long and I couldn't figure out what words to search for. Thanks so much!
Re: One grounded conductor per hole..... 110.14 (A) That's it. I haven't needed to read it in so long and I couldn't figure out what words to search for. Thanks so much!
raider1 Senior Member Staff member Location Logan, Utah Feb 14, 2006 #6 Re: One grounded conductor per hole..... 408.21 has changed to 408.41 in the 2005 NEC. The wording is the same just the numbering has changed. Chris
Re: One grounded conductor per hole..... 408.21 has changed to 408.41 in the 2005 NEC. The wording is the same just the numbering has changed. Chris
S speedypetey Senior Member Location Hudson Valley, NY Feb 14, 2006 #7 Re: One grounded conductor per hole..... Thanks. That's even better. I was searching the CD so it is hard to flip pages. I glanced right over that. I appreciate it guys.
Re: One grounded conductor per hole..... Thanks. That's even better. I was searching the CD so it is hard to flip pages. I glanced right over that. I appreciate it guys.