The NEC permits 'multi wire branch circuits', where the neutral is shared between several 'hot' conductors.
If you have a balanced three phase supply, then you can run three hot conductors with your standard size neutral.
Note however that the shared neutral must be in the same cable assembly as the hot conductors; you couldn't have the shared neutral in one MC cable, and the hots in another; you would need a single MC cable with one neutral and the three hots. You could have 3 hots and 1 neutral in conduit to a junction box, and then split out the neutrals to separate MC cables.
Your device boxes would need to be sized for all of the spliced conductors, and the breakers would need handle ties (under 2008 code). There are other rules about multi-wire branch circuits as well.