Re: Only 1 pole of a 2 pole breaker used
Steve when UL test two pole breakers it test them for a single pole to ground fault and for a single pole to neutral over load. If they didn't they would not need the slash rating as this is what it is there for. The slash rating is the voltage rating that the breaker may safely open a fault at the available fault current level that breaker is rated for. This can be many thousands of amps which could cause the breaker to fail to open. IE contacts weld or fail explosively.
We install two pole breakers all the time intended to serve single pole loads even you do it. Think! every main breaker, feeder breaker that feeds any panel will be feeding single pole loads. and to go one father, what about the UL listed combo device where you have a 120 volt receptacle and a 250 volt receptacle all on the same yoke? 210.4(C)Exception 2 not only allows this device but requires that it be fed from a two pole breaker.
If there was a safety problem using a two pole breaker to feed a single line to neutral load then the same problem would also be with any two pole breaker that feeds a sub panel.
Are we required to use a special two pole breaker to feed these sup panels? I think not.
As long as it has the 120/240 volt slash rating.
Is there a problem with certain ratings on breakers that would be a problem with this? Yes if the voltage rating exceeds the rating of the circuit it will slow too act in the event of an overload.
So don't use a 277/480 volt rated breaker to feed a 120/240 volt sub panel.
But you can use it to feed a multiwire 277 volt lighting circuit with no problems.
You cant use a straight rated breaker to feed a sub panel either.
This is why the NEC is silent on this is because it is done and has to be done in just about every installation. Just about every type of building there is a two pole breaker feeding single pole loads, The Main Breaker!
I have never seen a problem with it?
With that info, what you might have heard was crossed up with straight rated breakers, so I would say you have the requirement partly right. But it depends upon the rating of the breaker.
I hope this will clear this up.
[ October 29, 2005, 01:45 AM: Message edited by: hurk27 ]