sfav8r
Senior Member
- Location
- San Francisco Bay Area
I just installed new service to a 4-unit bldg. I ran 2/0 to a 4-gang meter box then used offset nipples to each load center. The problem is, I wasn't thinking about the fact that since there is no OCPD prior to each load center, I think I should have used rigid offset nipples instead of die-cast. Is that correct or can I avoid the hassle of going back and replacing the die-cast with rigid?
Thanks!