So I needed to get out of the wall and roughed in a two gang mud ring flush with the siding and now I want to extend it horizontally through a bell box extension ring but

They don't make a two gang bell box extension ring with three-quarter inch hubs coming
5eeb908ba3b4b07132a6282398fa9b3f.jpg

out the sides.
At least I couldn't find one.
Anyone have any idea

I could sweep down and make a U bend
but that wouldn't look as nice.

Here is actually the question
I remember when you put fluorescent lights in and the opening didn't line up with the 30 ring on the ceiling, one inspector said you could press a big hole in the sheet metal of the troffer to get in the 3/0
As long as you would still be able to see the entire 3/0 from below
What about putting a nema rated 6" sq box on the siding and pressing a 2 inches diameter opening the back of the box and landing a ground wire

Probably just better to bend the u bend for The listed rang :)

62e3ff94b3d213d0ffdbec4e966ac7cc.jpg



In belief, man can do anything
 

electricalist

Senior Member
Location
dallas tx
put on a 2g wp plate and chase nipple through it into what ever box you want.
Thats what i see.
Is the round wp extension ring for something surface mounted or is that the method to get to the 1 g bell box, a L L conduit body would do the same for you ..90 from the 1g into a L L or L R and you re there.
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
Thats what i see.
Is the round wp extension ring for something surface mounted or is that the method to get to the 1 g bell box, a L L conduit body would do the same for you ..90 from the 1g into a L L or L R and you re there.

The old round ring is what used to be mounted to the siding with some Romax in a conduit or some nonsense

it's going to be cut away but right now it's over a stairway

I like the Chase nipple and two single gang box because it'll be useful for a device


In belief, man can do anything
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I may be missing something, but they make WP box extension rings with hubs. If that is a possibility I would prefer that over blocking access to you box with a cover/chase nipple.
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
Exactly, I'm gonna come out of that piece and nipple down into the part that Augie found

For some reason I was hung up on the two gang box with horizontal 3/4" hub. Couldn't find that her sale anywhere

I can see the knockouts here in the picture you show. But I don't see the three-quarter horizontal hub on that two gang bell box extension ring