J jbriggs5 New User Location Kansas City, MO Occupation Superintendent Jan 18, 2024 #1 In an open air plenum is it ok to run liquid tight from junction box over to a VAV? If not would flexible metal conduit be the next best option? TIA
In an open air plenum is it ok to run liquid tight from junction box over to a VAV? If not would flexible metal conduit be the next best option? TIA
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 18, 2024 #2 300.22(C) I believe will be your guide and raceways with a overall non-metallic cover are not allowed,.. FMC is allowed.
300.22(C) I believe will be your guide and raceways with a overall non-metallic cover are not allowed,.. FMC is allowed.