ptonsparky
Tom
- EC - retired
We are changing out three services from what was three separate buildings to one service entrance and a feeder each to the other buildings. Two of the original services were single phase from the same transformer. The third was three phase 120/208 bank. All pole top transformers. The three phase hadn’t been used for ten years. The guys turned Off the 3 phase disconnect at the pole. Ran, the feeder and as they connected the EG noticed sparking. They took an amp reading of 5 amps. No doubt we paralleled the neutral back to the transformers, and assuming the primary neutral between the transformers. I will remove the three phase neutral bond tomorrow. That system is being Removed entirely next week. Transformers and all.
Clear as mud?
What would be the expected open circuit voltage when that bond is removed?
Clear as mud?