electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
We are all familiar with the figures that the capacity of the bank is .577 of what a full delta would be, or .866 of the KVA of the two transformers. Can we increase this value with strategic placement of loads? The "derating" is due to the poor internal power factor of this arrangement, but what Im not clear on is does that change depending on how we load the bank? For example say I connect a single phase L-L load across two of the closed phases. Can utilize the full nameplate KVA of that transformer? Unless I am missing something, It seems that I could, as that second transformer is just sitting there and does not need to be involved with that is going on.