Three-Phase, "open delta" transformer banks are only open delta on the secondary. The primary is open wye. Each of the two primaries are connected line-to-neutral.
As @LarryFine noted, this is the most common or universal "open delta" arrangement.
But there is no reason they couldn't be built with two bushing transformers connected line-line as two legs of a delta primary.
You can have 'open wye: open delta' (most common) or 'open delta: open delta' (rare, possibly never, but in theory perfectly possible).
-Jon