No, that would not work due to the multiple bonds to ground.
My mistake; between the meter and the xfmr. or are we talking about losing the neutral outside of those two points?
No, that would not work due to the multiple bonds to ground.
My mistake; between the meter and the xfmr. or are we talking about losing the neutral outside of those two points?
You would need to use a signal injection circuit similar to that used in some GFCIs to test whether you can specifically run current through the neutral wire. But the inline "transformers" (CTs) would have to be able to carry normal and fault neutral current as well.The OP seems to be talking about an open neutral between the utility transformer and the house.
Both ends of that will be bonded so detecting an open with a simple circuit is not possible.
You would need to use a signal injection circuit similar to that used in some GFCIs to test whether you can specifically run current through the neutral wire. But the inline "transformers" (CTs) would have to be able to carry normal and fault neutral current as well.
We could stop using grounded conductors for circuits or at least run equipment grounding conductors all the way back to the source on services and have no neutral to ground bonds beyond the source and eliminate many stray voltage and grounded neutral issues. I don't know how to get everyone else on board with either one of those ideas though.
That's a good thing to have if you service neutral ever goes bad.but then we have the metal water line to you neighbors house..... :dunce:
That's a good thing to have if you service neutral ever goes bad.