Re: open neutrals and voltage drop
------)(-----------B------------------>
 `````)(``````````````> 120V```````> load 1
 ``|``)(```````````````````````````>
  240V )(-----------N------------------|
 ```|`)(`````````````> 120V````````>
 `````)(```````````````````````````> load 2
 ------)(-----------A------------------>
    
 try to ignore all the ``` marks, had to space out the "drawing"
 
 Concidering the above transformer is a 1:1 ratio, you can see how an open in the neutral would give you 240V across both of the loads.
 
 
 in a resistive component heat is the power that component uses. for example, lets say  you have a 10 amps of 120V electricity flowing through a resistort. the ammount of power or heat you are producing is 1200w (P=IV). the resistor is heating up to whatever temperature it has to to pump out 1200 watts of energy (less temp if it's under water or air blowing on, or it's a large resistor). resistors can act one of two ways. as temperature goes up, so does resistance -or- as temperature goes up resitance goes down. these are positive and negative temperature coefficients. pretty much all conductors have a positive coefficient (temp up, resistance up) and have a "temperature curve" associated with their resistance. this is how RTDs (electronic temp detectors) work.