Open Wye Open Delta Connection
Re: Open Wye Open Delta Connection
paul32
The discussion I had with Charlie was related to high voltage, 15kv and up. Wye primary connections are fine, if you have a high voltage neutral, and and you ground the transformer high side neutral also. If you don't ground the high side neutral, during a single phase condition, the secondary line to neutral voltages can go crazy.
Your second question was relating to delta primary connections in wye systems. Delta-wye transformers are most common in low voltage applications, 480 to 120/208 volts for example, because the delta will tend to balance an imbalance in the wye, and present more of a balanced load to the 480 side. It also is effective in limiting the transfer of harmonics between the 208 side and the 480 side.
I don't think they are the most common in high voltage applications by a long shot.
Jim T
John, thanks for the clarification on xfmr polarities. Putting the little dots on the schematic really pins it down.
Finally found the book with an explanation of the open delta. They make the point that even with a resistive load, the open delta xfrmrs will operate at a PF less than unity. Of course you power guys already knew that.