Maybe need to search for ROP's back whenever this allowance was first introduced into code or for any times it has had changes to it to better understand why it is there. Yes they more recently removed the table that had been there for a long time and went to the 83% figure - but only thing that really did was made it more clear to applying adjustments like ambient temp or number of conductors in a raceway. without any adjustments you still run same size conductor you did using the old table.
What they have or more like how it applies it is not a demand factor. It also isn't an adjustment factor it is basically allowing us to use a different starting conductor ampacity in the situations described. How they come up with the 83% I don't know.
83% is 120% up-rating
120% is used in other areas of the code
i agree what they have is not a demand factor, but i think your interpretation is in line with a demand factor. (load diversification so we probably won't ever see that high of current)
again, thank you for your time and thoughts