Hello!! I'm doing optional load calculation of a townhouse structure that is made up of 3 stories. Below is my load calculation. Can the elevator and pool heater fall under the general load calculations as shown below? or do they need to be calculated as 100% like A/C units? I'm trying to stay below 200A panel. let me know what you think. Thank you!!
The condensor and AHU heater can be on at the same time (so that is why im adding both of their load in my calculation).
4000 SQFT
LTG and General Use at 3W/SF =12,000W
Ref. =1,000W
Range =12,000W
Dryer =5,000W
Dishwasher =1,200
Water Heater =4,500
Laundry =1,500
Appliance Circuit X2 =3,000
Microwave/hood =1,800
Elevator =4,000
Pool Heater =7,200
======================================
Total =53,200
======================================
First 10,000 W at 100% =10,000
Remainder of load 40% =17,280
======================================
AHU(with heat X 65%) =8,000
Condenser(100%) =12,000
===============================================
Total =47,280
At single phase 240/120V =197A