when using optional method do we consider the factor 1.25 for continous loads
K kimrichi Member Jan 20, 2013 #1 when using optional method do we consider the factor 1.25 for continous loads
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 20, 2013 #2 kimrichi said: when using optional method do we consider the factor 1.25 for continous loads Click to expand... Article 220 calcs, optional or regular method, do not call for continuous loads to have the 1.25 factor. The 1.25 factor for continuous loads comes into play when sizing the conductors and OCPD. A tad confusing I know, but that is the way the NEC is set up.
kimrichi said: when using optional method do we consider the factor 1.25 for continous loads Click to expand... Article 220 calcs, optional or regular method, do not call for continuous loads to have the 1.25 factor. The 1.25 factor for continuous loads comes into play when sizing the conductors and OCPD. A tad confusing I know, but that is the way the NEC is set up.