Just took my Supervisor's test in Bend, OR C.O.C.C, I wanted to help others who are taking this test. There were quite a few questions in article 605 and 820 in t he first portion of the test. In the second portion of the test I was given an industrial plant calculation that was all related to each other in this 12 question portion. I feel the first part of the test was easier, however this second part was very challenging so here it goes my questions:
1] What is the demand on a feeder for a 500x500 warehouse with 120 volt lighting and 500 general purpose receptacles. The service is 208/120 3 phase ? Here are the answer choices I was given
A.265
B.356
Are these figures Amps, VA, kVA, dollars spent on monthly electric bill????
C.251
D.229
2] What is the fault current available at the secondary terminals 1.8 impedance 500 KVA 480, 208/120 3 phase transforme
Details on the supply to the transformer? or are we assuming infinite bus ability for the purpose of this question?
3] Minimum size conductor in THWN per phase feeding 1200 amp 480 volt 3 phase load 1800 ft from source minimum 3% voltage drop?
Single conductor, parallel conductors? If parallel how many sets of parallels? Copper, aluminum?
This is the calculation from the whole part 2 of the exam:
480/277
535 KW lighting load
power factor?, or give me value in kVA please
2-250 HP 480 V motors
1- 480x208Y 120V 3 phase transformer that feeds:
5-10HP 208V 3 phase motors
3-25HP 208V 3 phase motors
17-20 amp punch press receptacles
voltage, number of phases? better yet actual load details of the machines, chances are they do not draw 20 amps.
8-30 amp receptacle
voltage, number of phases? better yet actual connected load 30 amp receptacle could only have 10 amps of load connected to it
250-general purpose receptacles
most will assume 15/20 amp 120 volt receptacles, but it would be nice if it were made clear that is what is intended.
I can't remember all the questions, this is just what is fresh in my head but all related to this. Anyone that can help me with this info I have here and do a regular calc? I was thrown off by the fact it was KW instead of VA... and the fact that there is receptacles listed separately from general purpose. How will I add in the 17 punch press receptacles and the 8/30 ampswr
As you can see I have similar questions - the exam was poorly written IMO. Like I said before it is sad when they give you a professional exam for a professional license, and they are not professional with the questions
Thanks for your time and help!