hillbilly1
- North Georgia mountains
- Owner/electrical contractor
A citation was issued in this case due to the marking on a portable GFCI device. An individual was using power from a hard wired GFCI receptacle outlet using an extension cord. He used a portable GFCI device as a splitter at the end of the extension cord. The portable device is marked to instruct the user to place the portable GFCI at the receptacle outlet. This marking exists on a portable device to ensure that the extension cord is also provided with GFCI protection. The marking however, applies only when the portable GFCI is the only GFCI protection provided.
There is no problem. There was no hazard. The level of protection was increased due to the open neutral protection provided by the portable GFCI device.
OSHA is removing the citation.
It should be noted that when a portable GFCI device is used on a non-GFCI protected circuit, it must be plugged into the receptacle outlet upstream of the extension cord or a valid citation will be issued.
That makes more sense, now that we have all of the details.