buffalonymann
- NC
181116-1035 EST
buffalonymann:
Were your measurements relative to common?
Relative to common, when fully stopped and stable in position, I would expect A+ relative to common to be somewhere near +5 or near 0. Near might mean +3.5 to +5, or 0 to 1.5+ .
Same would be true for B or Z. The receiving detector will look at the difference between A+ and A-. If slightly above a 0 difference that is one binary state, and if slightly below 0 difference that is the opposite binary state. This is called a balanced line system and has good immunity to common mode noise.
If both A+ and A- are +5 relative to common when the encoder is stable, then there is an internal problem. And with B+ and B- both at 2.5 V relative to common there is a different kind of problem.
If you monitor A+ relative to common and rotate the encoder is there any voltage change. I might expect somewhere near 2.5 V. Same check on A- relative to common.
I will be gone until late afternoon. There should be others that can help you.
I ended up cutting the encoder cable to about 5 ft long, used a 10k ohm pullup resistor across COMM and A+, used a power supply to power the encoder, and I was able to see the pulses. I suspect the encoder cable is damaged someplace along the route causing the issue.