Out building feed from house

Status
Not open for further replies.

jp480volt

Member
Location
Tucker, GA
We have an existing 60 amp single phase 3 wire UF cable from house panel.
Is it correct to drive new grounding electrodes and not bonding neutral?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Welcome to the forum!

It depends on what you are calling a "3-wire" cable. If you mean 3-wire plus ground (EGC) then yes, you need a GEC and separate neutrals/grounds. Also, the GEC has to land on the EGC bar.

If you mean 3-wires total, and if this is a new install, it's not allowed anymore. You would need the "4th" wire. In times past you could run the cable without ground (depending on circumstances such as no waterlines or other metallic paths between buildings) then bond the neutral to the cabinet along with the GEC.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We have an existing 60 amp single phase 3 wire UF cable from house panel.
Is it correct to drive new grounding electrodes and not bonding neutral?

Depends on what you mean by existing and if it's only 3 conductors. Prior to the 2008 NEC it was permitted to bond the neutral at a separate structure when that structure met a few conditions. If those conditions are met and it's prior to the adoption of the 2008 you can leave it and install a GES.
 

jp480volt

Member
Location
Tucker, GA
Welcome to the forum!

It depends on what you are calling a "3-wire" cable. If you mean 3-wire plus ground (EGC) then yes, you need a GEC and separate neutrals/grounds. Also, the GEC has to land on the EGC bar.

If you mean 3-wires total, and if this is a new install, it's not allowed anymore. You would need the "4th" wire. In times past you could run the cable without ground (depending on circumstances such as no waterlines or other metallic paths between buildings) then bond the neutral to the cabinet along with the GEC.

3-wire= (2-hots, 1-neutral NO EGC) wire is existing wire. Feeds well pump and lights.
7f0a09bf-d50f-4a80-b703-0a3a14328ab1

This shows neutral grounded again.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
3-wire= (2-hots, 1-neutral NO EGC) wire is existing wire. Feeds well pump and lights.
7f0a09bf-d50f-4a80-b703-0a3a14328ab1

This shows neutral grounded again.

The ground rod, equipment grounding conductor's and neutrals must all be bonded together in the panel at the outbuilding.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Not necessarily. As mentioned, the code changed in 2008, and many jurisdictions lag years behind. For example NY is still on 2014.
I think Steve was referring to the UF without an EGC. I used 10/3 NM without an EGC in the late 70's early 80's for dryers.

Roger
 