kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
2014 NEC no, earlier NEC yes, some exceptions - like if there is only a single branch circuit, then a snap switch is acceptable.If i have sub feed to a out building service rated equipment in the out building is not required ?
Yes, that requirement is and has been the same for some time. (it can possibly be up to six disconnecting means grouped at same location though).Sub feed to out building will i need a main disconnect at the out building?