I got a response back from the NFPA on my FI request. They didn't provide a formal answer, as I figured, but I did get an informal opinion from the Senior Electrical Engineer.
My question:
Concerning a hot tub installed outdoors does section 680.42(A)(2) supersede and thereby nullify section 680.22(A)(1)
Reply:
Section 6-1.4 (c) of the NFPA Regulations Governing Committee Projects does not permit a formal interpretation that involves text that clearly and decisively provides the requested information. However, I can provide some supporting information to assist you.
This is in reply to your email concerning the National Electrical Code? 2011.
No, the basic provision of 680.42 requires outdoor hot tub installations to comply with the provisions in Parts I and II of Article 680. Therefore, 680.22(A)(1) is applicable. Section 680.42(A)(2) permits the cord to be 15 ft long amending the 3 ft. length limitation required by 680.21(A)(5).
Mark Cloutier
NFPA Senior Electrical Engineer
Important notice! This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.