Outbuilding feeders and circuits from multiple locations

Status
Not open for further replies.

JoeNorm

Senior Member
Location
WA
Let's say we have an outbuilding with it's own sub-panel from a main house. The sub is not quite big enough to accommodate an addition that involves a new water heater(among other things). Can a circuit be run from a another location(closer) just to power the new water heater?

I recall there being a rule about not having multiple services, but this obviously is not that.
 
The simple answer is no, you cannot have two feeders supplying a structure, regardless of the source(s).
 
But a large circuit and a feeder wasn't the intention it was to allow for grouping of disconnects of the feeders like from a 320 meter with 2 disconnects
OK, but under the 2020 NEC as long as the feeders originate in the same panelboard, and the disconnects at the building are grouped, you can run a second feeder if desired, rather than upsize the existing feeder. Just use a disconnect with OCPD at the building, then even if the circuit goes on to supply just one piece of equipment (the water heater), the supply to the building is still a feeder.

Cheers, Wayne
 
OK, but under the 2020 as long as the feeders originate in the same panelboard, and the disconnects at the building are grouped, you can run a second feeder if desired, rather than upsize the existing feeder. Just use a disconnect with OCPD at the building, then even if the circuit goes on to supply just one piece of equipment (the water heater), the supply to the building is still a feeder.

Cheers, Wayne
I feel like this is waiting for issues once there's more clarification in future code cycles
 
I feel like this is waiting for issues once there's more clarification in future code cycles
Why? It says what it says. It doesn't say "equal size feeders" or anything like that. If the disconnects are grouped and labeled as required, what's the problem?

Cheers, Wayne
 
Why? It says what it says. It doesn't say "equal size feeders" or anything like that. If the disconnects are grouped and labeled as required, what's the problem?

Cheers, Wayne
Wasn't allowed for a long time it's just asking for someone to say it's unsafe even if its completely safe and was only allowed to make it easier to be compliant with emergency disconnect rules.
 
Wasn't allowed for a long time it's just asking for someone to say it's unsafe even if its completely safe and was only allowed to make it easier to be compliant with emergency disconnect rules.
Allowing more than one feeder to a second building has ZERO to do with the emergency disconnect rule in 230.85. While it applies to all second buildings, this change was aimed at second buildings that require a large amount of power. The idea is to reduce the arc flash hazard at the second building. The incident energy available at each of the multiple second building disconnects will be less than the incident energy that would be available at a single second building disconnect.
 