My first post on the forum, I read the NEC rule regarding the feeder taps ( 10ft, 25 ft rules ). However the situation is like this.
4 single family dwellings connected to one service feeder. After the entrance to the houses the cables run about 40 feet in the house then enter distrubition panels and protected by 125A circuit breakers. The problem is when you want to change any of the breakers you need to turn off all 4 houses from a 400A breaker. The 4/0 cable comes in front of the 4 houses and is spliced to the four houses with 1/0 cable which they run like 100 ft.
Isn't this a code violation ? What can be done to fix the issue ? My concern would be , the 400A breaker protecting 1/0 cables, in case of a overload in the house side ( say 160A ) the 400A breaker won't trip but the cable will heat up.
Any comments appreciated.
4 single family dwellings connected to one service feeder. After the entrance to the houses the cables run about 40 feet in the house then enter distrubition panels and protected by 125A circuit breakers. The problem is when you want to change any of the breakers you need to turn off all 4 houses from a 400A breaker. The 4/0 cable comes in front of the 4 houses and is spliced to the four houses with 1/0 cable which they run like 100 ft.