Outdoor Outlets Required

Status
Not open for further replies.

horses

Member
I'm in the process of doing an independent living project & there are no outlets shown on the drawings for the living units on the ground floor that have patio's. My question is are they required? beings this is an independent living facility or does it fall ubder 210.52E? The engineer did'nt show any on the patio's.

Thanks
 
Recpt's

Recpt's

Always be carefull of the phrases used in the spec's. " to be to the NEC or according to the local AHJ", these are usually boiler plate statements (I'm paraphrasing of course) These statements cover the engineer and the architect.
 
horses said:
I'm in the process of doing an independent living project & there are no outlets shown on the drawings for the living units on the ground floor that have patio's. My question is are they required?
Point of interest.... NEC 2008 will require receptacles on all "balconies, decks, and porches" as per 210.52(E)(3), not just those at ground level. Only exception is if the usable area is less than 20 sq ft.

My guess is this will trip up lots of people doing weekend warrior deck projects...
 