Re: Outdoor Pool Pump Wiring
In the 1999 cycle the NEC required the equipment grounding conductor to be 12 AWG and insulated,
680.25 (c) Motors. Pool-associated motors shall be connected to an equipment grounding conductor sized in accordance with Table 250-122 but not smaller than No. 12. It shall be an insulated copper conductor
It went on to say that in a dwelling unit PVC or EMT was required.
In 2002 there was changes made to 680 where .21 came into being,
680.21 (A) (1) General. The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the location. Other wiring methods and materials shall be permitted in specific locations or applications as covered in this section. Any wiring method employed shall contain a copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.
And for a dwelling unit:
Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
Edited to add?-- the word insulated is missing in (A) (1) leads some to believe that a UF cable would be acceptable
Now we have the 2005 which says,
680.21 (A) (1) Any wiring method employed shall contain an insulated copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.
And for a dwelling unit,
In the interior of one-family dwellings,????.. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
I agree with the NM cable on the inside of a dwelling unit but, the underground EGC got to have insulation before and after the 2002 cycle. This is adding support for those who debate the insulated EGC for 2002. personally I like the insulated EGC myself
[ April 16, 2005, 07:53 PM: Message edited by: jwelectric ]