outdoor receptacle

Status
Not open for further replies.
Re: outdoor receptacle

No, the small appliance circuit used to serve the dining room receptacle outlets shall serve no other outlets except as permitted in section 210.52(B)(1).

An outdoor receptacle would not qualify as one of the listed areas.
 
Re: outdoor receptacle

You list yourself as an electrician? signed on today and posted a question like that?How long in the trade?
 
Re: outdoor receptacle

Is this dinning room outlet on the small appliance circuit?

If it is on some other general purpose circuit then I would say yes. If it is on the small appliance circuit then no for reasons stated above.


a.wayne3@verizon.net,
{edit}
I'm sorry, I was out of line for posting what previously filled this space. every place I have worked talking trash is considered part of the trades. It is always taken lightly and never personal. I do, however, understand why on a forum it must be prohibited.
{/edit}

[ August 30, 2004, 10:09 PM: Message edited by: Local ]
 
Re: outdoor receptacle

a.wayne3, how long you been in the trade? and whats wrong with the question?
 
Re: outdoor receptacle

can a receptacle in the dining room supply an outside outlet? just wondering about wording ?
no other outlets on dining room circuit i agree.
 
Re: outdoor receptacle

Not every outlet in a dining room is or must be on the small appliance branch circuit. It is permissible to put dinning room receptacles on the small appliance branch circuit but it is not required. Dinning room outlets may be fed by a general purpose circuit.
 
Re: outdoor receptacle

Local,
Even if you feed the dining room with it's own dedicated branch circut(as my company does), you still could not feed an outdoor w/p receptacle off of it.
See Bryan's post above.
 
Re: outdoor receptacle

livewirek1

From my own experience, just when we think we understand a code section, some exception or obscure reference will alter our opinion. Your post had me refering to 210.52(B), but as the other guys said, (edited)- the answer seems to be no.

Buck

[ September 02, 2004, 12:57 PM: Message edited by: buck33k ]
 
Re: outdoor receptacle

Originally posted by Local: It is permissible to put dinning room receptacles on the small appliance branch circuit but it is not required.
I disagree. Here is my view:
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">If you are standing in a dining room, and see a receptacle on a wall, then it is there specifically because 210.52(A) required it to be installed.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">210.52(B) says that the 2 or more SA circuits shall supply everything in 210.52(A).</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, the dining room receptacle is on the SA circuit.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">QED</font>
<font size="2" face="Verdana, Helvetica, sans-serif">To take it one step further, if you install a new breaker, and run a dedicated branch circuit that supplies one receptacle outlet in the dining room, and that supplies nothing else, then that new circuit becomes, by definition, a small appliance circuit.
 
Re: outdoor receptacle

You list yourself as an electrician? . . . How long in the trade?
How long you been in the trade? And what?s wrong with the question?
These remarks are close to being personal in nature, and unfriendly in character. Please don?t go there. Let?s write all our questions and comments in a professional tone.
 
Re: outdoor receptacle

i was changing the wording only , because if there was a receptacle just for a/c, i don't see the issue of it going outside also. thanks !
 
Re: outdoor receptacle

Ok, I've gone back over the pertinent sections and it looks like I'm wrong. I was definitely wrong by using the word permissible it is required that the SA circuit supply the dinning room. It has been some time since I've done residential and it looks like I need to study some more.

That being said, I do not see where the code prohibits circuits other then the required SA circuits to feed an outlet in the dinning area. However, after consideration I can understand why an inspector may not allow this, as a home owner may plug in devices we consider small appliances into these circuits because they are there. However just because an outlet is in a location does not mean it all the sudden becomes something it is not. Do you disagree with that Charlie B? Nothing personal but I do not think it becomes something it isn't just because of its existence.

We must keep in mind the code is just a minimum and if you go above and beyond you are still ok. Years ago we were allowed to provide GP circuits and outside outlets in areas that also must have a SA circuit or some other requirement. Maybe times have changed and maybe I'm out of the loop on new residential.I do find this a much more interesting thought then AFCI debates as I am not a fan, in the least, of AFCI's.
 
Re: outdoor receptacle

OK Local, cudos on your edit.

Now, I, for one will agree with you that Once the REQUIRED receptacles are installed in the dining room, it would be permissable to add others that would not by default become SA circuts.
One example would be receptacles under the window as part of a 'Holiday Package', that we often install.

But on the reverse, these cannot be included in the wall space requirements of the SA circut.
 
Re: outdoor receptacle

cs409 its been 31 long years,210.52 (1) % (2)
do not allow you to tag a wp gfci or any other receptacle off this circuit unless listed in that section.
 
Re: outdoor receptacle

Charlie b:

I have to disagree with your proof.

If you are standing in a dining room, and see a receptacle on a wall, then it is there specifically because 210.52(A) required it to be installed.
The receptacle may be there for other reasons. It may be there per 210.70(A)(1), in which case it would not be on a small appliance circuit

Steve :)

[ August 31, 2004, 09:19 AM: Message edited by: steve66 ]
 